A service has three parallel sets of 400 kcmil copper per phase. What is the minimum copper GEC to building steel?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5022
- B: 3/0 AWG
Explanation
The equivalent area is 3 x 400 = 1200 kcmil, which exceeds 1100 kcmil. Table 250.66 requires a 3/0 copper GEC for copper service conductors over 1100 kcmil.