In NEC 2026, the 1 1/2 in spacing rule for wiring methods under roof decking applies to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6016
- D: All types of roof decking
Explanation
NEC 2026 300.6(E) removed the limitation to metal-corrugated decking, so the spacing applies under all roof decking. A new exception covers wiring methods encased in at least 2 in of concrete.
More questions: Wiring Methods, Conductors and Boxes
- 6017Where ungrounded conductors 4 AWG or larger enter an enclosure through a raceway, what is required at the entry?
- 6018NEC 2026 added a requirement in 300.4 for conductors and wiring methods that have been
- 6019EMT must be securely fastened within what distance of each outlet box, junction box, or termination?
- 6020What is the maximum distance between supports for EMT under the general rule?
- 6021Rigid metal conduit must generally be secured within what distance of each box or termination?
- 6022Trade size 1 rigid PVC conduit must be supported at intervals not exceeding