A conduit run between two boxes has two 90 degree bends and four 30 degree offset bends. How many more degrees of bend may be added before a pull point is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6035
- C: 60 degrees
Explanation
The run already has 2 x 90 + 4 x 30 = 300 degrees. The limit between pull points is 360 degrees, so only 60 degrees more may be added. See the bend rules in the raceway articles (300.24 in NEC 2026).