A receptacle is replaced in a dwelling bedroom where the current code requires tamper-resistant receptacles. What must be installed?

Exactly one answer is correct.

Show solution

Correct answer to question 7011

  • A: A tamper-resistant receptacle

Explanation

Section 406.4(D)(5) (406.12(D) in NEC 2026) requires replacements to be tamper-resistant where 406.12 (406.26 in NEC 2026) calls for tamper-resistant receptacles. The age of the wiring does not matter.