Question 7033 of 731 · Texas Journeyman Electrician Exam
A plug-in circuit breaker is back-fed to supply a panelboard. How must it be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7033
- A: Secured by an additional fastener that requires more than a pull to release it
Explanation
Section 408.36(D) requires back-fed plug-in breakers to be secured in place by an additional fastener that requires other than a pull to release. Otherwise a breaker with energized line terminals could be pulled off the bus.
More questions: Equipment, Devices and Luminaires
- 7034What is the maximum rating of the overcurrent device protecting a panelboard?
- 7035In a commercial building, a panelboard is supplied by a feeder from another panel. What must the panelboard be marked with?
- 7036In a panelboard supplied by a 4-wire delta system with a high leg, which phase position must the high leg occupy?
- 7037In a dwelling unit, where are overcurrent devices such as a panelboard not permitted?
- 7038Which type of luminaire is not permitted in a clothes closet?
- 7039What is the minimum clearance between a surface-mounted LED luminaire with a completely enclosed light source and the closet storage space?