A permanently connected appliance rated above 300 VA is not within sight of its branch-circuit breaker. What is required?

Exactly one answer is correct.

Show solution

Correct answer to question 7053

  • D: The breaker must be lockable open with a permanent locking provision

Explanation

Section 422.31(B) allows the branch-circuit switch or breaker as the disconnect if it is within sight of the appliance or can be locked in the open position. The locking provision must stay in place whether or not the lock is installed.