A flexible cord is run from one room to another through a hole in the wall. Is this permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7059
- C: No, cords may not be run through holes in walls, ceilings or floors
Explanation
Section 400.12 prohibits running flexible cords through holes in walls, structural ceilings, suspended ceilings, dropped ceilings or floors. Cords may also not be concealed behind walls or attached to building surfaces.