Question 8002 of 731 · Texas Journeyman Electrician Exam
A continuous-duty motor has a table full-load current of 28 A. What is the minimum ampacity of its branch-circuit conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8002
- D: 35 A
Explanation
Section 430.22 requires 125 percent of the table full-load current. 28 A times 1.25 equals 35 A. 32.2 A would result from wrongly using 115 percent.
More questions: Motors, HVAC, Generators and Transformers
- 8003When sizing motor branch-circuit conductors and short-circuit protection for a general-purpose motor, which current must be used?
- 8004Which value is used to size separate motor overload protection?
- 8005A motor with a marked service factor of 1.15 needs a separate overload device. What is the maximum rating as a percentage of nameplate full-load current?
- 8006A motor is marked with a temperature rise of 40 degrees C. What overload rating is permitted as a percentage of nameplate current?
- 8007A motor has a service factor of 1.0 and no temperature rise marking. What is the maximum overload rating?
- 8008A motor with a service factor of 1.0 has a nameplate current of 20 A. What is the maximum separate overload setting under 430.32(A)(1)?