A 20 kW, 240 volt single-phase generator supplies a distribution panel. What is the minimum ampacity of the conductors from the generator terminals to the first overcurrent device?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8053
- C: 95.8 A
Explanation
The nameplate current is 20,000 W divided by 240 V, which is 83.3 A. Section 445.13(A) requires 115 percent, so 83.3 A times 1.15 gives 95.8 A. 104.2 A would result from wrongly using 125 percent.