A 75 kVA dry-type transformer is installed indoors. What is the minimum separation from combustible material without a fire-resistant barrier?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8068
- D: 12 in
Explanation
Section 450.21(A) requires dry-type transformers of 112.5 kVA or less installed indoors to have at least 12 in of separation from combustible material, unless a fire-resistant, heat-insulating barrier is used. Transformers of 1000 volts or less that are completely enclosed are exempt.