Question 8076 of 731 · Texas Journeyman Electrician Exam
What is the minimum ampacity of conductors supplying a capacitor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8076
- D: 135 percent of the capacitor rated current
Explanation
Section 460.8(A) requires capacitor circuit conductors to have an ampacity of at least 135 percent of the rated current of the capacitor. Capacitor current rises with voltage and harmonics.
More questions: Motors, HVAC, Generators and Transformers
- 8078Why are capacitors installed in motor circuits in industrial plants?
- 8001Branch-circuit conductors supplying a single continuous-duty motor must have an ampacity of at least what percentage of the motor full-load current?
- 8002A continuous-duty motor has a table full-load current of 28 A. What is the minimum ampacity of its branch-circuit conductors?
- 8003When sizing motor branch-circuit conductors and short-circuit protection for a general-purpose motor, which current must be used?
- 8004Which value is used to size separate motor overload protection?
- 8005A motor with a marked service factor of 1.15 needs a separate overload device. What is the maximum rating as a percentage of nameplate full-load current?