What is the general fire resistance rating required for transformer vault walls and roofs?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8073
- D: 3 hours
Explanation
Section 450.42 generally requires walls and roofs of transformer vaults to have adequate structural strength and a minimum fire resistance of 3 hours. Where vaults are protected by automatic sprinklers or similar systems, 1 hour construction is permitted.