Under NEC 2026, what additional load must the emergency electrical disconnect at a motor fuel dispensing facility shut off?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9023
- D: Receptacles located over or adjacent to the dispenser
Explanation
NEC 2026 revised 514.11(A) so the emergency disconnect also removes power from receptacles over or adjacent to the dispenser. In a fuel leak or spill, a plugged-in appliance there could otherwise act as an ignition source.