Question 9029 of 731 · Texas Journeyman Electrician Exam
In health care facilities, a patient care space where failure of equipment or the electrical system is likely to cause major injury or death is which category?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9029
- A: Category 1 (critical care)
Explanation
Category 1 spaces are critical care spaces where failure is likely to cause major injury or death. Category 2 failures are likely to cause minor injury, Category 3 failures are not likely to cause injury, and Category 4 spaces are support spaces.
More questions: Special Occupancies
- 9030A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
- 9031Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?
- 9035The essential electrical system of a hospital is divided into which branches?
- 9036Article 518 for assembly occupancies applies to buildings or portions of buildings designed for the gathering of how many persons or more?
- 9039At a carnival, circus, or fair, 125-volt, single-phase, 15- and 20-ampere receptacles used by personnel or readily accessible to the public require what protection?
- 9057On a construction site, a 125-volt, single-phase, 20-ampere receptacle on a temporary power pole used by workers requires what protection?