What is the minimum rating of the service equipment or feeder assembly supplying a mobile home?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9045
- A: 100 amperes
Explanation
Mobile home service equipment and the feeder assembly to the home must be rated at not less than 100 amperes at 120/240 volts. A listed 50-ampere power supply cord is a separate option for the home connection.