In agricultural buildings, which receptacles generally require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9043
- A: Receptacles in areas with an equipotential plane, outdoors, and in damp or wet locations
Explanation
Article 547 requires GFCI protection for receptacles in areas having an equipotential plane, outdoors, in damp or wet locations, and in dirt confinement areas for livestock. Barns combine moisture, conductive floors, and animal contact.