What is the minimum size of the copper conductor used to bond an equipotential plane in an agricultural building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9042
- C: 8 AWG solid copper
Explanation
The equipotential plane is bonded to the building electrical grounding system with a solid copper conductor not smaller than 8 AWG, which may be insulated, covered, or bare. The plane itself uses wire mesh or other conductive elements embedded in the concrete.