Question 9041 of 850 · Texas Journeyman Electrician Exam
In an agricultural building, an equipotential plane is required in which area?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9041
- A: Indoor livestock confinement areas with concrete floors where metallic equipment is accessible to livestock
Explanation
Equipotential planes are required in livestock confinement areas with concrete floors that contain metallic equipment accessible to animals and likely to become energized. Livestock are very sensitive to small voltage differences, so the plane keeps floor and equipment at the same potential.