A code-required system supplies sewage disposal pumps and smoke removal equipment during outages, with less urgency than egress lighting. Which system is this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11017
- D: Legally required standby (Article 701)
Explanation
Legally required standby systems serve loads such as heating and refrigeration, communications, ventilation and smoke removal, sewage disposal, and industrial processes that could create hazards if stopped. They must have power within 60 seconds.