Egress lighting required by a building code to illuminate exit paths during a power outage is part of which system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11016
- C: Emergency system (Article 700)
Explanation
Illumination for safe exiting and exit signs are classic emergency system loads. They must be restored within 10 seconds.