In assembly occupancies for more than 1000 persons or buildings above 75 ft in height, emergency feeder circuit wiring must have what protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11013
- A: A minimum 2-hour fire rating or equivalent protection
Explanation
Emergency feeder wiring in these occupancies must be protected by a 2-hour fire-rated assembly, fire-resistive cable system, or other listed methods. The feeders must keep working during a fire.