Standard method (NEC 2026), 120/240 V: 2,400 ft2 dwelling, two small-appliance and one laundry circuit, 1,200 VA dishwasher, 900 VA disposal, 4,500 W water heater, 1,000 VA trash compactor, 12 kW range, 5.5 kW dryer, 9 kW electric heat and 4,800 VA AC. What is the minimum calculated service load in amperes?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12008
- D: 139.2 A
Explanation
Lighting/SA/laundry 9,300 VA with demand = 5,205 VA; four fixed appliances 7,600 VA x 75 % = 5,700 VA; range 8,000 VA; dryer 5,500 VA; heat 9,000 VA (AC omitted as noncoincident). Total 33,405 VA / 240 V = 139.2 A (Table 120.45, 120.53, Table 120.55).