Five 12 kW household ranges in an apartment building are on one feeder. What range demand load is used under the NEC 2026?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12049
- A: 20 kW
Explanation
Table 120.55 Column C gives 20 kW for five ranges of not over 12 kW. The nameplate total of 60 kW is not used.
More questions: Load Calculations
- 12050What is the NEC 2026 Column C demand for ten 12 kW ranges?
- 12051A 30-unit apartment building has a 12 kW range in each unit. Using NEC 2026 Table 120.55 Column C, what is the range demand load?
- 12052Under the NEC 2026, a 6 kW counter-mounted cooktop and two 3 kW wall ovens in the same kitchen share one branch circuit. What is the branch circuit load?
- 12053Ten ranges supply an apartment building: five rated 11 kW and five rated 14 kW. What is the range demand load under the NEC 2026?
- 12054Under the NEC 2026, an 8 kW range demand load is part of a 120/240 V dwelling feeder. What neutral load is assigned to the range?
- 12055A 120/240 V feeder has a calculated maximum unbalanced load of 350 A. What is the NEC 2026 neutral load after the permitted reduction?