Five 12 kW household ranges in an apartment building are on one feeder. What range demand load is used under the NEC 2026?

Exactly one answer is correct.

Show solution

Correct answer to question 12049

  • A: 20 kW

Explanation

Table 120.55 Column C gives 20 kW for five ranges of not over 12 kW. The nameplate total of 60 kW is not used.