Question 12055 of 931 · Texas Journeyman Electrician Exam

A 120/240 V feeder has a calculated maximum unbalanced load of 350 A. What is the NEC 2026 neutral load after the permitted reduction?

Exactly one answer is correct.

Show solution

Correct answer to question 12055

  • C: 305.0 A

Explanation

The first 200 A of unbalanced load counts at 100 % and the portion above 200 A at 70 % (120.61): 200 + 150 x 0.70 = 305 A. Nonlinear loads would prevent this reduction.

Next to question ›