A 10-unit apartment building has 1,000 ft2 units, each with two small-appliance circuits and one laundry circuit. What is the NEC 2026 standard method demand for lighting, small-appliance and laundry loads on the service?

Exactly one answer is correct.

Show solution

Correct answer to question 12058

  • B: 24,700 VA

Explanation

Per unit: 1,000 x 2 VA + 4,500 VA = 6,500 VA; ten units = 65,000 VA. The demand factors apply to the total (Table 120.45): 3,000 + 62,000 x 0.35 = 24,700 VA.