Under the NEC 2026 optional calculation for an existing dwelling (120.83), how are the existing general loads treated?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12061
- A: First 8 kVA at 100 %, rest at 40 %
Explanation
120.83 uses a single table in the 2026 edition: the first 8 kVA of load counts at 100 % and the remainder of the existing load at 40 %. New loads are then added with their own factors.
More questions: Load Calculations
- 12062Under the NEC 2026 existing dwelling calculation (120.83), at what percentage is a newly added EVSE counted?
- 12063A dwelling has 7.5 kW of electric baseboard heat and a 6,000 VA central AC unit that never run at the same time. What load is used under the NEC 2026 standard method?
- 12064A retail store has 80 general-purpose receptacle outlets (single yokes). What is the NEC 2026 receptacle load after demand factors?
- 12065An office has 50 general-purpose duplex receptacles. What receptacle load is used in the NEC 2026 service calculation?
- 12066A store has 30 linear feet of show window. What show window lighting load applies in an NEC 2026 feeder calculation?
- 12067What minimum load is used for a required sign outlet at a commercial entrance under the NEC 2026?