An office has 50 general-purpose duplex receptacles. What receptacle load is used in the NEC 2026 service calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12065
- A: 9,000 VA
Explanation
50 x 180 VA = 9,000 VA (120.14(I)). The 50 % demand factor applies only to the portion above 10 kVA, so the full 9,000 VA is used.
More questions: Load Calculations
- 12066A store has 30 linear feet of show window. What show window lighting load applies in an NEC 2026 feeder calculation?
- 12067What minimum load is used for a required sign outlet at a commercial entrance under the NEC 2026?
- 12068A 25 ft fixed multioutlet assembly in a lab will not have its appliances used at the same time. What load applies under the NEC 2026?
- 12069A gallery has 40 ft of lighting track. What minimum track lighting load is used in an NEC 2026 feeder calculation?
- 12070A 12,000 ft2 office building is calculated under the NEC 2026 using the unit load of 1.3 VA per ft2. What is the general lighting load?