A gallery has 40 ft of lighting track. What minimum track lighting load is used in an NEC 2026 feeder calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12069
- A: 3,000 VA
Explanation
Track lighting is counted at 150 VA for every 2 ft of track or fraction in the Article 120 Part III lighting rules: 40 / 2 = 20 x 150 = 3,000 VA.
More questions: Load Calculations