What general lighting load applies to a 6,000 ft2 retail store under the NEC 2026 unit load table?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12071
- C: 11,400 VA
Explanation
Retail occupancies take 1.9 VA per ft2 (Table 120.42(A)): 6,000 x 1.9 = 11,400 VA. The 2 VA value of 120.41 is for dwelling units only.
More questions: Load Calculations
- 12072A restaurant kitchen has five pieces of electric cooking equipment rated 14, 10, 8, 5 and 3 kW. What is the NEC 2026 feeder demand load for this equipment?
- 12073A commercial kitchen has six units rated 20, 15, 2, 2, 1 and 1 kW. What feeder demand load applies under the NEC 2026?
- 12074A warehouse has a general lighting load of 30,000 VA. What is the demand load under the NEC 2026 lighting demand factors?
- 12001Using the standard method under the NEC 2026, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?
- 12002A 2,000 ft2 dwelling has the minimum two small-appliance circuits and one laundry circuit. Under the NEC 2026 standard method, what is the demand load for general lighting, small-appliance and laundry loads combined?
- 12003A 3,200 ft2 one-family dwelling has three 20 A small-appliance circuits and one laundry circuit. Under the NEC 2026 standard method, what is the net demand load for these loads plus general lighting?