A restaurant kitchen has five pieces of electric cooking equipment rated 14, 10, 8, 5 and 3 kW. What is the NEC 2026 feeder demand load for this equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12072
- D: 28 kW
Explanation
The total is 40 kW. For five units the commercial kitchen demand factor is 70 % (Table 120.56): 40 x 0.70 = 28 kW, which is above the 24 kW of the two largest units, so 28 kW stands.
More questions: Load Calculations
- 12073A commercial kitchen has six units rated 20, 15, 2, 2, 1 and 1 kW. What feeder demand load applies under the NEC 2026?
- 12074A warehouse has a general lighting load of 30,000 VA. What is the demand load under the NEC 2026 lighting demand factors?
- 12001Using the standard method under the NEC 2026, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?
- 12002A 2,000 ft2 dwelling has the minimum two small-appliance circuits and one laundry circuit. Under the NEC 2026 standard method, what is the demand load for general lighting, small-appliance and laundry loads combined?
- 12003A 3,200 ft2 one-family dwelling has three 20 A small-appliance circuits and one laundry circuit. Under the NEC 2026 standard method, what is the net demand load for these loads plus general lighting?
- 12004Under the NEC 2026 standard method, what is the demand load for general lighting, two small-appliance circuits and one laundry circuit in a 4,500 ft2 dwelling?