A commercial kitchen has six units rated 20, 15, 2, 2, 1 and 1 kW. What feeder demand load applies under the NEC 2026?

Exactly one answer is correct.

Show solution

Correct answer to question 12073

  • A: 35 kW

Explanation

Six or more units take 65 % (Table 120.56): 41 x 0.65 = 26.65 kW. The demand may not be less than the two largest units combined, 20 + 15 = 35 kW, so 35 kW is used.