A 12,000 ft2 office building is calculated under the NEC 2026 using the unit load of 1.3 VA per ft2. What is the general lighting load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12070
- B: 15,600 VA
Explanation
Table 120.42(A) assigns offices 1.3 VA per ft2: 12,000 x 1.3 = 15,600 VA. Older editions used 3.5 VA, and 1.9 VA is the retail value.
More questions: Load Calculations