A dwelling has 7.5 kW of electric baseboard heat and a 6,000 VA central AC unit that never run at the same time. What load is used under the NEC 2026 standard method?

Exactly one answer is correct.

Show solution

Correct answer to question 12063

  • C: 7,500 VA

Explanation

Noncoincident loads (120.6) allow the smaller of two loads that will not operate together to be omitted. The larger heating load, 7,500 VA, is used at 100 % in the standard method.