A dwelling has 7.5 kW of electric baseboard heat and a 6,000 VA central AC unit that never run at the same time. What load is used under the NEC 2026 standard method?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12063
- C: 7,500 VA
Explanation
Noncoincident loads (120.6) allow the smaller of two loads that will not operate together to be omitted. The larger heating load, 7,500 VA, is used at 100 % in the standard method.