A store has 30 linear feet of show window. What show window lighting load applies in an NEC 2026 feeder calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12066
- B: 6,000 VA
Explanation
Show window lighting is counted at not less than 200 VA per linear foot of window measured horizontally (120.14(G)): 30 x 200 = 6,000 VA.
More questions: Load Calculations
- 12067What minimum load is used for a required sign outlet at a commercial entrance under the NEC 2026?
- 12068A 25 ft fixed multioutlet assembly in a lab will not have its appliances used at the same time. What load applies under the NEC 2026?
- 12069A gallery has 40 ft of lighting track. What minimum track lighting load is used in an NEC 2026 feeder calculation?
- 12070A 12,000 ft2 office building is calculated under the NEC 2026 using the unit load of 1.3 VA per ft2. What is the general lighting load?
- 12071What general lighting load applies to a 6,000 ft2 retail store under the NEC 2026 unit load table?
- 12072A restaurant kitchen has five pieces of electric cooking equipment rated 14, 10, 8, 5 and 3 kW. What is the NEC 2026 feeder demand load for this equipment?