A retail store has 80 general-purpose receptacle outlets (single yokes). What is the NEC 2026 receptacle load after demand factors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12064
- D: 12,200 VA
Explanation
Each yoke counts at 180 VA (120.14(I)): 80 x 180 = 14,400 VA. Non-dwelling receptacle loads may take the first 10 kVA at 100 % and the rest at 50 % under the Article 120 receptacle demand table: 10,000 + 4,400 x 0.5 = 12,200 VA.