Under the NEC 2026 existing dwelling calculation (120.83), at what percentage is a newly added EVSE counted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12062
- B: 80 %
Explanation
The 2026 table of 120.83 counts new EVSE and new central electric resistance heating at 80 %, while other new loads count at 50 % and the existing load beyond 8 kVA at 40 %.
More questions: Load Calculations
- 12063A dwelling has 7.5 kW of electric baseboard heat and a 6,000 VA central AC unit that never run at the same time. What load is used under the NEC 2026 standard method?
- 12064A retail store has 80 general-purpose receptacle outlets (single yokes). What is the NEC 2026 receptacle load after demand factors?
- 12065An office has 50 general-purpose duplex receptacles. What receptacle load is used in the NEC 2026 service calculation?
- 12066A store has 30 linear feet of show window. What show window lighting load applies in an NEC 2026 feeder calculation?
- 12067What minimum load is used for a required sign outlet at a commercial entrance under the NEC 2026?
- 12068A 25 ft fixed multioutlet assembly in a lab will not have its appliances used at the same time. What load applies under the NEC 2026?