A 5.5 kW household dryer is on a 120/240 V service. What is its neutral load under the NEC 2026?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12057
- A: 3,850 VA
Explanation
The dryer counts at 5,500 VA (larger of 5,000 VA or nameplate, 120.54). The neutral load for dryers is 70 % of that (120.61): 5,500 x 0.70 = 3,850 VA.
More questions: Load Calculations