Ten ranges supply an apartment building: five rated 11 kW and five rated 14 kW. What is the range demand load under the NEC 2026?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12053
- A: 26.25 kW
Explanation
For unequal ratings over 8.75 kW, ranges under 12 kW are counted as 12 kW and the average is found (Table 120.55, Note 2): (5 x 12 + 5 x 14) / 10 = 13 kW. That is 1 kW over 12, so Column C (25 kW for ten) rises 5 %: 25 x 1.05 = 26.25 kW.