Question 13015 of 731 · Texas Journeyman Electrician Exam
A single-phase 240 volt load draws 50 amperes, and a wattmeter reads 10.2 kW. What is the power factor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13015
- C: 0.85
Explanation
Apparent power is 240 x 50 = 12,000 VA, so PF = W / VA = 10,200 / 12,000 = 0.85. A power factor above 1.0 (1.18) results from dividing VA by W and cannot occur.
More questions: Electrical Calculations
- 13016A 5 kW resistance heater runs 8 hours per day. At $0.12 per kWh, what does one day of operation cost?
- 13017A 15 kW balanced three-phase resistive heater is connected to 208 volts. What is the line current?
- 13018A 120/240 volt single-phase 3-wire feeder carries 40 A on one ungrounded conductor and 25 A on the other. Assuming linear loads, what current flows in the neutral?
- 13019A 3-phase 4-wire wye feeder has linear loads of 50 A on phase A, 40 A on phase B and 30 A on phase C. What is the approximate neutral current?
- 13020What is the line-to-neutral voltage of a 480Y/277 volt system, calculated from the 480 volt line-to-line value?
- 13021Each winding of a balanced delta-connected load carries 20 amperes. What is the line current?