Question 3005 of 731 · Texas Journeyman Electrician Exam
When may a feeder OCPD be sized at 100 percent of the continuous load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3005
- C: When the assembly and its OCPD are listed for operation at 100 percent of their rating
Explanation
The exception allows 100 percent sizing only where the assembly, including the OCPD, is listed for continuous operation at 100 percent of its rating. See 215.3 Exception.
More questions: Feeders and Overcurrent Protection
- 3006In which case is the next size up rule not permitted?
- 3007The available fault current at a panelboard is 18,000 A. Which breaker interrupting rating is acceptable?
- 3008What is the maximum rating of a plug fuse?
- 3009A feeder is protected at 400 A. What is the minimum copper THWN tap conductor at 75 degrees C for a 25 ft tap?
- 3010What is the maximum height of the center of the operating handle of a circuit breaker in its highest position?
- 3011A 400 A feeder OCPD protects a feeder. Field-installed 10 ft tap conductors leave the enclosure. What is the minimum tap ampacity?