A 400 A feeder OCPD protects a feeder. Field-installed 10 ft tap conductors leave the enclosure. What is the minimum tap ampacity?

Exactly one answer is correct.

Show solution

Correct answer to question 3011

  • B: 40 A

Explanation

One-tenth of 400 A is 40 A. The tap must also be at least the combined calculated load and not less than the rating of the device it supplies. See 240.21(B)(1).