A 400 A feeder OCPD protects a feeder. Field-installed 10 ft tap conductors leave the enclosure. What is the minimum tap ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3011
- B: 40 A
Explanation
One-tenth of 400 A is 40 A. The tap must also be at least the combined calculated load and not less than the rating of the device it supplies. See 240.21(B)(1).