In which case is the next size up rule not permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3006
- D: A multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads
Explanation
The next higher standard rating may not be used for multioutlet branch circuits supplying receptacles for portable cord-and-plug-connected loads. See 240.4(B)(1).