Question 3022 of 731 · Texas Journeyman Electrician Exam
A feeder supplies 100 A of continuous load and 30 A of noncontinuous load. What is the minimum feeder conductor ampacity before any adjustment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3022
- A: 155 A
Explanation
Feeder conductors must have an ampacity of at least 125 percent of the continuous load plus 100 percent of the noncontinuous load. 100 A times 1.25 is 125 A, plus 30 A gives 155 A. See 215.2(A)(1).