Question 3024 of 731 · Texas Journeyman Electrician Exam
Unless specifically permitted elsewhere, what is the maximum OCPD for 12 AWG copper conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3024
- A: 20 A
Explanation
The small conductor rule limits 14 AWG copper to 15 A, 12 AWG copper to 20 A and 10 AWG copper to 30 A. See 240.4(D).
More questions: Feeders and Overcurrent Protection
- 3025A feeder conductor has an ampacity of 115 A and does not supply receptacles for portable loads. What is the largest standard OCPD permitted under the next size up rule?
- 3026GFPE is required for a feeder disconnect rated 1000 A or more on which system?
- 3027Unless specifically permitted elsewhere, what is the maximum OCPD for 14 AWG copper conductors?
- 3028Three parallel sets of conductors give a total ampacity of 1140 A. What is the largest standard OCPD permitted?
- 3029Which standard OCPD rating comes directly after 800 A?
- 3030A circuit breaker has an interrupting rating other than what value must be marked with that rating?