Three parallel sets of conductors give a total ampacity of 1140 A. What is the largest standard OCPD permitted?

Exactly one answer is correct.

Show solution

Correct answer to question 3028

  • C: 1000 A

Explanation

Above 800 A the next size up rule does not apply, so the OCPD must not exceed the conductor ampacity. The largest standard rating not over 1140 A is 1000 A. See 240.4(C) and 240.6(A).