Question 3029 of 731 · Texas Journeyman Electrician Exam
Which standard OCPD rating comes directly after 800 A?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3029
- D: 1000 A
Explanation
In the list of standard ratings, 800 A is followed by 1000 A and then 1200 A. There is no 900 A standard rating. See 240.6(A).
More questions: Feeders and Overcurrent Protection