A circuit breaker used to switch 120 volt fluorescent lighting on a regular basis must be marked with which designation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3051
- A: SWD or HID
Explanation
Breakers used as switches in 120 volt and 277 volt fluorescent lighting circuits must be listed and marked SWD or HID. HID breakers may also switch high-intensity discharge lighting. See 240.83(D).