When 90 C rated THHN conductors are installed with 75 C terminations, what is the 90 C ampacity used for?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4108
- D: As the starting value for adjustment and correction factors
Explanation
110.14(C) allows conductors with higher temperature ratings to use their higher ampacity for ampacity adjustment, correction or both. The final result may not exceed the ampacity at the termination temperature.