For a circuit rated over 100 amperes with conductors larger than 1 AWG, which temperature column may be used for termination purposes unless equipment is marked otherwise?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4107
- D: 75 C
Explanation
110.14(C)(1)(b) permits conductors for circuits rated over 100 amperes, or larger than 1 AWG, to be used at their 75 C ampacity. Higher values apply only when the termination is listed for them.