Question 4106 of 731 · Texas Journeyman Electrician Exam
An 8 AWG copper THHN conductor connects to terminals rated 75 C on both ends. What ampacity may be used for the circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4106
- A: 50 amperes
Explanation
8 AWG copper is 40 A at 60 C, 50 A at 75 C and 55 A at 90 C. The 90 C insulation does not help because the 75 C terminals limit the conductor to 50 A under 110.14(C).
More questions: Branch Circuits, GFCI and AFCI
- 4107For a circuit rated over 100 amperes with conductors larger than 1 AWG, which temperature column may be used for termination purposes unless equipment is marked otherwise?
- 4108When 90 C rated THHN conductors are installed with 75 C terminations, what is the 90 C ampacity used for?
- 4109How may a 10 AWG grounded conductor be identified?
- 4110A 2 AWG grounded conductor has black insulation. How may it be identified as the grounded conductor?
- 4112A white conductor in a cable assembly is used as an ungrounded conductor for a switch loop. What does the NEC require?
- 4001In a dwelling unit, GFCI protection is required for all 125-volt through 250-volt receptacles installed in which of the following locations?